A 1500 KVA three-phase transformer has a secondary voltage of 480/277. What is its secondary full load amperage?

Prepare for the NCCER Industrial Maintenance Electrical and Instrumentation Test. Study with practice questions and explanations. Boost your readiness for the exam!

To calculate the secondary full load amperage of a three-phase transformer, you can use the following formula:

[ I = \frac{P}{\sqrt{3} \times V}

]

Where:

  • ( I ) is the full load amperage,
  • ( P ) is the power in kilovolt-amperes (KVA),
  • ( V ) is the voltage in volts.

Given that the transformer has a power rating of 1500 KVA and a secondary voltage of 480 volts (line-to-line voltage for a three-phase system), you would substitute these values into the formula.

First, calculate the full load amperage using the 480 V:

  1. Convert KVA to VA: [ P = 1500 \times 1000 = 1,500,000 \text{ VA} ]

  2. Apply the values in the formula: [ I = \frac{1,500,000}{\sqrt{3} \times 480} ]

  3. Calculate ( \sqrt{3} ) which is approximately 1.732. [ I = \frac{1,