In a 1000 KVA three-phase transformer with a secondary voltage of 206/120, what is the secondary full load amperage?

Prepare for the NCCER Industrial Maintenance Electrical and Instrumentation Test. Study with practice questions and explanations. Boost your readiness for the exam!

To determine the secondary full load amperage of a three-phase transformer, you can use the formula for calculating the full load current (I) in a three-phase system. The formula is:

[ I = \frac{KVA \times 1000}{\sqrt{3} \times V} ]

where KVA is the transformer capacity, and V is the secondary voltage line-to-line.

In this case, the transformer has a capacity of 1000 KVA and a secondary voltage of 206 volts (line-to-line). Plugging these values into the formula, we perform the following calculation:

  1. Convert KVA to watts: ( 1000 KVA = 1000 \times 1000 = 1,000,000 , \text{watts} ).
  2. Calculate the full load current:

[ I = \frac{1000 \times 1000}{\sqrt{3} \times 206} ]

  1. The value of (\sqrt{3}) is approximately 1.732. Now substituting that value:

[ I = \frac{1,000,000}{1.732 \times 206} ]

  1. Calculating the denominator